Register Name / Module Address | Assembled Address for PLC | Description |
---|---|---|
Upstream Module Status 4:0134 |
M: 4:1714 E: I.Data [14] P: Byte 28 (Hi) Byte 29 (Lo) |
Interger Value of Low or High Byte: 0×01 = Zone sensor clear and motor stopped 0×02 = Zone sensor clear, motor running, accepting from upstream zone 0×04 = Zone sensor blocked, motor running, discharging to downstream zone 0×05 = Zone sensor blocked and motor stopped 0×06 = Busy (state during ConveyStop active mode) |
Downstream Module Status 4:0232 |
M: 4:1715 E: I.Data [15] P: Byte 30 (Hi) Byte 31 (Lo) |
|
Current Tracking Word 1 for Adjacent Upstream Module 4:0139 |
M: 4:1716 E: I.Data [16] P: Byte 32 (Hi) Byte 33 (Lo) |
Value = Tracking data word #1 (16-bit integer) for the Carton that has just discharged from the module adjacent to this local module |
Current Tracking Word 2 for Adjacent Upstream Module 4:0140 |
M: 4:1717 E: I.Data [17] P: Byte 34 (Hi) Byte 35 (Lo) |
Value = Tracking data word #2 (16-bit integer) for the Carton that has just discharged from the module adjacent to this local module |
Reserved | M: 4:1718 E: I.Data [18] P: Byte 36 (Hi) Byte 37 (Lo) |
Used for Reset Protection connection See topic Assemblies with Reset Protection for details |
Understanding Adjacent Modules
These registers only contain meaningful data if the ConveyLinx connections between upstream and/or downstream modules are preserved when placing the local module into PLC I/O mode from within EasyRoll. If connections are cleared in EasyRoll, these registers will not contain any pertinent data and will not be updated by adjacent modules. Learn about clearing connections.