Register Name / Module Address Assembled Address for PLC Description
Left Motor Run / Reverse
4:0260
M: 4:1804
E: O.Data [4]
P: Byte 8 (Hi)
   Byte 9 (Lo)
Bit 0:
   1 = Run Command
   0 = Stop Command
Bit 8:
   0 = Run in Configured Direction
   1 = Run opposite of Configured Direction
Left Motor Brake Method
4:0261
M: 4:1805
E: O.Data [5]
P: Byte 10 (Hi)
   Byte 11 (Lo)
Integer Value:
   1 = Use Standard Brake Method
   2 = Use Free Coast Brake Method
   3 = Use Servo Brake Method
   4 = Use Continuous Torque
   0 = Remain at last configured or last value entered
Left Motor Slave Mode
4:0262
M: 4:1806
E: O.Data [6]
P: Byte 12 (Hi)
   Byte 13 (Lo)
Integer Value:
   0 = Ignore
   1 = Slave Mode OFF – Left motor independently controlled from Right
   2 = Slave Mode ON – Left motor mirrors Right motor control
   3 = Slave Mode ON – Left motor runs in opposite direction of Right motor
Left Motor Speed Reference
4:0040
M: 4:1810
E: O.Data [10]
P: Byte 20 (Hi)
   Byte 21 (Lo)
Integer Value
   For MDR value is in mm/s
  For PGD value is in RPM X 10
   0 = Remain at last non zero value entered
Left Motor Acceleration
4:0043
M: 4:1812
E: O.Data [12]
P: Byte 24 (Hi)
   Byte 25 (Lo)
Integer Value
   For MDR value is in mm
   For PGD value is in motor pulses

   Deceleration Range: 0 to 10000 (Both MDR and PGD)
   Acceleration Range: 30 to 10000 (Both MDR and PGD)
   0 = Remain at last non-zero value entered
Left Motor Deceleration
4:0044
M: 4:1813
E: O.Data [13]
P: Byte 26 (Hi)
   Byte 27 (Lo)