Module Configuration Tabs / Sensors / ConveyLinx-Ai Family /
Accumulate Intermediate Zones |
ConveyLinx ERSC ❌ | ConveyLinx-Ai 24V ✅ | ConveyLinx-Ai 48V ✅ |
ConveyLinx-ECO ❌ | ZPA Mode ✅ | PLC I/O Mode ❌ | |
By default, and without intervention; all zones in between the most upstream and most downstream zones always try to convey items downstream if the next downstream zone is clear. To cause an intermediate zone to accumulate based upon a wired signal, you need to utilize the Aux I/O Pin 2 signal for the zone in questions as an Accumulate input.
Assuming the intermediate zone we want to accumulate is the upstream zone and the upstream zone is connected to the Left side of the module; we set the Left Aux I/O Pin 2 to Accumulate from the drop down box and make sure we click the “UP” arrow to indicate that the Left Pin 2 signal is to be associated with the Upstream Zone. When the Left Pin 2 is energized, the upstream zone will accumulate the next item that arrives |
How to change the zone where the PIN 2 signal is used
The PIN 2 signal does not have to be associated with the zone being controlled by the side of the module where you want to connect the signal. The diagonal arrows shown below the drop-down boxes all you to route the particular PIN 2 signal to the opposite zone.
For example we want to use the Left PIN 2 signal to accumulate the downstream zone which happens to be connected to the Right side of the module. We set the Left PIN 2 to Accumulate(DI) from the drop down box and make sure we click the diagonal arrow to point to the Downstream zone on the module. When the Left AUX is energized, the downstream zone will accumulate the next item that arrives |