PLC Developers Guide / PLC I/O Mode Control / PLC Outputs for PLC I/O Mode /
Set Status & Tracking |
ConveyLinx ERSC ✅ | ConveyLinx-Ai 24V ✅ | ConveyLinx-Ai 48V ✅ |
ConveyLinx-ECO ✅ | ZPA Mode ❌ | PLC I/O Mode ✅ | |
Register Name | Internal Address | Assembled PLC Address | Description | ||
Set Status to Downstream Module |
4:0196 | M: 4:1817 E: O.Data [17] P: Byte 34 (Hi) P: Byte 35 (Lo) |
Integer Value | ||
Used to write this module’s ZPA Status to its neighboring Downstream module | |||||
4 = | Instruct Downstream module to “wake-up” and run its most upstream zone | ||||
1 = | Instructs Downstream module that carton has exited local zone and to accept any tracking data written in Set Discharge Tracking Word 1 / Word 2 registers when carton arrives | ||||
Set Status to Upstream Module |
4:0116 | M: 4:1818 E: O.Data [18] P: Byte 36 (Hi) P: Byte 37 (Lo) |
Integer Value | ||
Used to write this module’s ZPA Status to its neighboring Upstream module | |||||
5 = | Instructs Upstream module’s discharge zone to accumulate and hold any carton that arrives at its discharge zone | ||||
1 = | Instructs Upstream module’s discharge zone to release any carton that arrives at its discharge zone | ||||
Set Discharge Tracking Word 1 | 4:0201 | M: 4:1820 E: O.Data [20] P: Byte 40 (Hi) P: Byte 41 (Lo) |
Integer Value | ||
Only used when local PLC I/O Mode module needs to pass tracking data Word 1 to a Downstream connected ConveyLinx Module. Used in conjunction with Set Status to Downstream Module register | |||||
Set Discharge Tracking Word 2 | 4:0202 | M: 4:1821 E: O.Data [21] P: Byte 42 (Hi) P: Byte 43 (Lo) |
Integer Value | ||
Only used when local PLC I/O Mode module needs to pass tracking data Word 2 to a Downstream connected ConveyLinx Module. Used in conjunction with Set Status to Downstream Module register | |||||
Reserved | N/A | M: 4:1822 E: O.Data [22] P: Byte 44 (Hi) P: Byte 45 (Lo) |
Reserved |