PLC Developers Guide / PLC I/O Mode Control / PLC Inputs for PLC I/O Mode /


Right Motor Status

ConveyLinx ERSC ConveyLinx-Ai 24V ConveyLinx-Ai 48V
ConveyLinx-ECO ZPA Mode PLC I/O Mode

Register Name Internal Address Assembled PLC Address Description
Right Motor Current 4:0079 M: 4:1708
E: I.Data [8]
P: Byte 16 (Hi)
P: Byte 17 (Lo)
Integer Value
Right Motor Current in mA
Example: 1900 = 1.9 Amps
Right Motor Frequency 4:0080 M: 4:1709
E: I.Data [9]
P: Byte 18 (Hi)
P: Byte 19 (Lo)
Integer Value
Right Motor electrical frequency in Hz
Example: 300 = 300 Hz
Right Motor Temperature 4:0081 M: 4:1710
E: I.Data [10]
P: Byte 20 (Hi)
P: Byte 21 (Lo)
Byte-Wise Integer Value
Byte encoded value of temperatures in °C
 High Byte = Right Motor temperature
 Low Byte = Internal Right Motor Driver temperature
Right Motor Status 4:0082 M: 4:1711
E: I.Data [11]
P: Byte 22 (Hi)
P: Byte 23 (Lo)
Bitwise Value
Bit 00 = Motor Rotation Status
Bit 01 = Motor Rotation Status
Bit 02 = Port in Digital Mode
Bit 03 = Reserved
Bit 04 = Reserved
Bit 05 = Board Overheat
Bit 06 = Over-Voltage
Bit 07 = Low Voltage
Bit 08 = Over-Heated
Bit 09 = Over-Current
Bit 10 = Short Circuit
Bit 11 = Motor Not Connected
Bit 12 = Overloaded
Bit 13 = Stalled
Bit 14 = Hall Sensor Error
Bit 15 = 2 See Note
1 Real Speed
Right Motor
4:0508 M: 4:1724
E: I.Data [24]
P: Byte 48 (Hi)
P: Byte 49 (Lo)
1 Motor Speed and Speed Status
Bit 00 – Bit 13 = Numerical value of Right motor’s current speed
 ● For MDR value is in mm/sec
 ● For PGD value is in RPM x 10
Bit 14 = Set when Right Motor speed is above its maximum speed
Bit 15 = Set when Right Motor speed is below its minimum speed

1 Motor Speed and Speed Status is only available for ConveyLinx-Ai Family controllers.


2 Bit 15 Usage

Motor Rotation Status

Motor Frequency

Motor Real Speed