PLC Developers Guide / ZPA Mode Control / PLC Outputs for ZPA Mode /
Release and Status |
ConveyLinx ERSC ✅ | ConveyLinx-Ai 24V ✅ | ConveyLinx-Ai 48V ✅ |
ConveyLinx-ECO ✅ | ZPA Mode ✅ | PLC I/O Mode ❌ | |
Register Name | Internal Address | Assembled PLC Address | Description | |
Release and Accumulate on Next Arrival for Local Upstream Zone | 4:0105 | M: 4:1608 E: O.Data [8] P: Byte 16 (Hi) P: Byte 17 (Lo) |
When bit 0 of Accumulation Control for Local Upstream Zone is set: | |
Changing the value in this register will cause the Carton accumulated in this zone to release and the zone will be armed to automatically accumulate the next Carton that arrives | ||||
Release and Accumulate on Next Arrival for Local Downstream Zone | 4:0185 | M: 4:1609 E: O.Data [9] P: Byte 18 (Hi) P: Byte 19 (Lo) |
When bit 0 of Accumulation Control for Local Downstream Zone is set: | |
Changing the value in this register will cause the Carton accumulated in this zone to release and the zone will be armed to automatically accumulate the next Carton that arrives | ||||
Set Status for Upstream Induct | 4:0134 | M: 4:1610 E: O.Data [10] P: Byte 20 (Hi) P: Byte 21 (Lo) |
Only used when local module is accepting loads from Non-ConveyLinx controlled conveyor: | |
Set value to 4 to cause the local upstream zone to run to accept the Carton being delivered by the non-ConveyLinx controlled conveyor. Set value to 1 to cause the local upstream zone to accept the tracking data written in Set Induct Tracking Word 1 / Word 2 | ||||
Set Status for Downstream Discharge | 4:0232 | M: 4:1611 E: O.Data [11] P: Byte 22 (Hi) P: Byte 23 (Lo) |
Only used when local module is discharging loads to Non-ConveyLinx controlled conveyor: | |
Set value to 5 to cause the local downstream zone to accumulate and hold any Carton that arrives Set value to 1 to allow the local downstream zone to release the Carton |