PLC Developers Guide / PLC I/O Mode Control / PLC Inputs for PLC I/O Mode /
Input Status |
ConveyLinx ERSC ✅ | ConveyLinx-Ai 24V ✅ | ConveyLinx-Ai 48V ✅ |
ConveyLinx-ECO ✅ | ZPA Mode ❌ | PLC I/O Mode ✅ | |
Register Name | Internal Address | Assembled PLC Address | Description | ||
Sensor Detect | 4:0036 | M: 4:1702 E: I.Data [2] P: Byte 4 (Hi) P: Byte 5 (Lo) |
Bitwise Value | ||
bit 00 = | Device is connected to Right Sensor Port | ||||
bit 01 = | Device is connected to Left Sensor Port | ||||
All other bits reserved | |||||
Module Voltage | 4:0024 | M: 4:1703 E: I.Data [3] P: Byte 6 (Hi) P: Byte 7 (Lo) |
Value in mV of Module Power Supply | ||
Range: 0 to 35000 1 | |||||
Example: 23500 = 23.5 Volts |
1 For 48V ConveyLinx Modules the range is up to 50000 mV (50V). Please note that if your PLC Assembly Data Registers are formatted as a Signed Integer, the largest positive 16 bit number visible in your register is 32767 (32.767 V). If you view this register as a Signed Integer, then 48000 (48V) will display as -17536. Please make sure you perform the proper data type functions on the Module Voltage register so that you are viewing and operating on an Unsigned Integer