PLC Developers Guide / ZPA Mode Control / PLC Inputs for ZPA Mode
Arrival/Departure Counts |
ConveyLinx ERSC ✅ | ConveyLinx-Ai 24V ✅ | ConveyLinx-Ai 48V ✅ |
ConveyLinx-ECO ✅ | ZPA Mode ✅ | PLC I/O Mode ❌ | |
Register Name | Internal Address | Assembled PLC Address | Description | |
Arrival Count Local Upstream Zone |
4:0106 | M: 4:1502 E: I.Data [2] P: Byte 4 (Hi) P: Byte 5 (Lo) |
Unsigned Integer Value | |
● Increments by 1 each time a carton arrives in the zone | ||||
Arrival Count Local Downstream Zone |
4:0186 | M: 4:1504 E: I.Data [4] P: Byte 8 (Hi) P: Byte 9 (Lo) |
● Value rolls over from 65,535 back to 0 | |
Departure Count Local Upstream Zone |
4:0107 | M: 4:1503 E: I.Data [3] P: Byte 6 (Hi) P: Byte 7 (Lo) |
Unsigned Integer Value | |
● Increments by 1 each time a carton departs in the zone | ||||
Departure Count Local Downstream Zone |
4:0187 | M: 4:1505 E: I.Data [5] P: Byte 10 (Hi) P: Byte 11 (Lo) |
● Value rolls over from 65,535 back to 0 | |