PLC Developers Guide / ZPA Mode Control / PLC Outputs for ZPA Mode / Set Outputs /

ConveyLinx-Ai Family


Set Port Outputs

ConveyLinx ERSC ConveyLinx-Ai 24V ConveyLinx-Ai 48V
ConveyLinx-ECO ZPA Mode PLC I/O Mode

Register Name Internal Address Assembled PLC Address Description
Set Aux I/O Outputs 4:0063 M: 4:1617
E: O.Data [17]
P: Byte 34 (Hi)
P: Byte 35 (Lo)
Bitwise Value
bit 08 = Left Aux I/O (Pin 2) Usage:
0 = Use as Input / 1 = Use as Output
bit 09 = Right Aux I/O (Pin 2) Usage:
0 = Use as Input / 1 = Use as Output
bit 12 = Left Aux I/O (Pin 2) as Output:
1 = ON, 0 = OFF (only if bit 08 is ON)
bit 13 = Right Aux I/O (Pin 2) as Output:
1 = ON, 0 = OFF (only if bit 09 is ON)
All other Bits reserved

Aux I/O Outputs for ConveyLinx-Ai Family

In certain applications, it may be desired to have the PLC actuate a device along the conveyor (i.e. illuminate a light or energize a solenoid coil, etc.). With the ConveyLinx network this can be done without installing a separate PLC I/O system to do this. Refer to either the EasyRoll+ or EasyRoll documentation on how to configure the Aux I/O output.