Tag Name Data Type Module Register Bit Description
I_ConveyStopByLostConnection BOOL 4:0019 6 Stop active due to lost communication connection
I_ConveyStopByPLCCmd BOOL 4:0019 10 Stop active due to Stop Command from PLC
I_ConveyStopByPLCDisconnect BOOL 4:0019 7 Stop active due to lost PLC connection
I_ConveyStopByRemoteModule BOOL 4:0019 5 Stop active on other module in Stop Group
I_Current_Left_MDR REAL 4:0055 - Current Draw of Left MDR in Amps
I_Current_Right_MDR REAL 4:0079 - Current Draw of Right MDR in Amps
I_Dig_Mtr_Over_Cur_Left BOOL 4:0060 14 Left: More than 1A detected on one or more outputs
I_Dig_Mtr_Over_Cur_Right BOOL 4:0084 14 Right: More than 1A detected on one or more outputs
I_Dig_Mtr_Short_Cir_Left BOOL 4:0060 12 Left: Short Circuit Error on one or more outputs
I_Dig_Mtr_Short_Cir_Right BOOL 4:0084 12 Right: Short Circuit Error on one or more outputs
I_Frequency_Left_MDR INT 4:0056 - Frequency of Left MDR in Hz
I_Frequency_Right_MDR INT 4:0080 - Frequency of Right MDR in Hz
I_Heartbeat BOOL 4:0035 15 Module Heartbeat, 2s On / 2s Off
I_Module_Enabled BOOL - AOI Logic Local Outputs are Enabled (Reset Protection Mode)
I_Motor_Sts_Left INT 4:0058 - Left Module Status
I_Motor_Sts_Right INT 4:0082 - Right Module Status
I_Sensor_Detect_Left_Port BOOL 4:0036 1 Sensor Detected on Left Pin 4
I_Sensor_Detect_Right_Port BOOL 4:0036 0 Sensor Detected on Right Pin 4
I_Sensor_Port_Left_Pin2 BOOL 4:0035 0 Left Sensor Port Pin 2 Energized ( if used as input )
I_Sensor_Port_Left_Pin4 BOOL 4:0035 4 Left Sensor Port Pin 4 Energized
I_Sensor_Port_Right_Pin2 BOOL 4:0035 2 Right Sensor Port Pin 2 Energized ( if used as input )
I_Sensor_Port_Right_Pin4 BOOL 4:0035 6 Right Sensor Port Pin 4 Energized
I_Servo_CmdComplete_Left BOOL 4:0011 0 1 = Last Servo Run Command Complete
I_Servo_CmdComplete_Right BOOL 4:0016 0 1 = Last Servo Run Command Complete
I_Servo_CmdStatus_Left BOOL 4:0011 2 1 = Running to Pulse Command Position
I_Servo_CmdStatus_Right BOOL 4:0016 2 1 = Running to Pulse Command Position
I_Servo_Position_Left INT 4:0062 - Signed Integer Value for Position from Position “0”
I_Servo_Position_Right INT 4:0086 - Signed Integer Value for Position from Position “0”
I_Speed_Left INT 4:0507 - Value in mm/sec for MDR or RPM x 10 for PGD Range: depends upon the Ai MDR or PGD connected MDR Example: 400 = 0.40 m/s PGD Example : 400 = 40 RPM 0 = Remain at last non zero value entered
I_Speed_Left_Max BOOL 4:0507 14 Left Motor Set Speed is Greater Than Motor Maximum
I_Speed_Left_Min BOOL 4:0507 15 Left Motor Set Speed is Less Than Motor Minimum
I_Speed_Right INT 4:0508 - Value in mm/sec for MDR or RPM x 10 for PGD Range: depends upon the Ai MDR or PGD connected MDR Example: 400 = 0.40 m/s PGD Example : 400 = 40 RPM 0 = Remain at last non zero value entered
I_Speed_Right_Max BOOL 4:0508 14 Right Motor Set Speed is Greater Than Motor Maximum
I_Speed_Right_Min BOOL 4:0508 15 Right Motor Set Speed is Less Than Motor Minimum
I_Temp_MDR_Left INT 4:0057 Hi Byte Left Motor Temperature Reading
I_Temp_MDR_Right INT 4:0081 Hi Byte Right Motor Temperature Reading
I_Temp_On_Board_Left INT 4:0057 Lo Byte Left On Board Temperature Reading
I_Temp_On_Board_Right INT 4:0081 Lo Byte Right On Board Temperature Reading
I_Tracking_UpZn DINT 4:0139 (MSW)
4:0140 (LSW)
AOI Logic Tracking for Load Discharged from Adjacent Upstream Module
I_Voltage_MDR REAL 4:0024 - Voltage Measured on MDR Power Connection
I_Zone_Status_DnModule INT 4:0232 - Local Downstream Status
I_Zone_Status_UpModule INT 4:0134 - Local Upstream Status