Before changing the voltage selection jumper, shut down ATevo and lock out ac and dc power supplies. Turning off (opening) the ATevo internal circuit breakers does not eliminate live voltages inside the enclosure.

STEPS

  • Standard needle-nosed pliers are required.
  • Remove the ATevo safety shield per Section 2.2, Removing Protective Safety Shield.
  • Locate the multi-tap terminal block.
  • Set locations of RED jumpers for desired ac input voltage, per Section 2.3.2, Verifying Multi-Tap AC Input Voltage Setting.
    • Carefully pry out both jumpers in existing locations.
    • Re-install jumpers into new (correct) locations.
    • Do NOT unscrew and adjust ATevo internal wiring at jumper terminal block (TB-H#).
  • Re-check jumper locations and confirm jumpers are properly seated.
Last modified: 11 September 2025