PLC Developers Guide / PLC I/O Mode Control / PLC Outputs for PLC I/O Mode / Left Motor Control /

ConveyLinx-Ai Family


Left Motor Control

ConveyLinx ERSC ConveyLinx-Ai 24V ConveyLinx-Ai 48V
ConveyLinx-ECO ZPA Mode PLC I/O Mode

Register Name Internal Address Assembled PLC Address Description
Run / Reverse
Left Motor
4:0260 M: 4:1804
E: O.Data [4]
P: Byte 8 (Hi)
P: Byte 9 (Lo)
Bitwise Value
Bit 00 :
 1 = Run Command
 0 = Stop Command
Bit 08 :
 0 = Run in Configured Direction
 1 = Run opposite of Configured Direction
Set Brake Method
Left Motor
4:0261 M: 4:1805
E: O.Data [5]
P: Byte 10 (Hi)
P: Byte 11 (Lo)
Integer Value
1 = Use Standard Brake Method
2 = Use Free Coast Brake Method
3 = Use Servo Brake 1 Method
4 = Use Continuous Torque Method
0 = Remain at last configured or last value entered
Set Slave Mode
Left Motor
4:0262 M: 4:1806
E: O.Data [6]
P: Byte 12 (Hi)
P: Byte 13 (Lo)
Integer Value
0 = Ignore
1 = Slave Mode OFF
2 = Slave Mode ON – Left = Right Motor
3 = Slave Mode ON – Left opposite of Right
Set Speed Reference
Left Motor
4:0040 M: 4:1810
E: O.Data [10]
P: Byte 20 (Hi)
P: Byte 21 (Lo)
Integer Value
MDR = Value is in mm/sec
PGD = Value is in RPM x 10
0 = Remain at last non-zero value entered
Set Acceleration
Left Motor
4:0043 M: 4:1812
E: O.Data [12]
P: Byte 24 (Hi)
P: Byte 25 (Lo)
Integer Value
MDR = Value is in mm
PGD = Value is in Motor Pulses
Range = 30 to 10000
0 = Remain at last non-zero value entered
Set Deceleration
Left Motor
4:0044 M: 4:1813
E: O.Data [13]
P: Byte 26 (Hi)
P: Byte 27 (Lo)
Integer Value
MDR = Value is in mm
PGD = Value is in Motor Pulses
Range = 0 to 10000
0 = Remain at last non-zero value entered