STEP 1: Add the Module to the PLC Network

From the Catalog window, drag and drop the ConveyLinx-Ai DAP into the Network View window
To attach the module to the PLC, click on the Not Assigned link and select the desired Profinet Interface of the PLC
When attached, you will see the green graphic linking the PLC and the module together

STEP 2: Assign the EXACT Profinet Name to the Module

In the Project Tree locate your newly created module under the Ungrouped devices folder. Right Click on your module to show a pop-up menu and select Properties
A new window will open. Select General from the menu on the left. In the Name field enter the required name for the device. In our example it is conveylinxzpa-0-20 from the Example Table
Type in the EXACT Profinet Name and press enter to make the change

STEP 3: Enter the I.P. Address

In the same properties area that you changed the Profinet Name, click on Ethernet addresses and enter the I.P. address. In our example it is 192.168.0.20 from the Example Table

STEP 4: Select Update Time Interval

In the same properties area that you changed the Profinet Name, click on Advanced options and select a proper Update Time. For a ConveyLinx module in ZPA mode, the recommended Update time should be between 32ms and 512ms.