STEP 1: Add the Module to the PLC Network

From the Catalog window, drag and drop the ConveyLinx-Ai in reduced ZPA mode DAP into the Network View window
To attach the module to the PLC, click on the Not Assigned link and select the desired Profinet Interface of the PLC
When attached, you will see the green graphic linking the PLC and the module together

STEP 2: Assign the EXACT Profinet Name to the Module

Follow the same STEP 2 as in Full ZPA Example. For this example the correct Profinet Name per our Example Table is conveylinxzpa-101-22

STEP 3: Enter the I.P. Address

Follow the same STEP 3 as in Full ZPA Example. For this example the correct I.P. Address per our Example Table is 192.168.101.22

STEP 4: Select Update Time Interval

Follow the same STEP 4 as in Full ZPA Example. Because this module is in ZPA mode, the recommended Update time to be between 32ms and 512ms.