For some PLC controllers, the data size footprint required for a given assembly can be a limiting factor on how many devices can connect to a given controller. ConveyLinx includes input/output assemblies with fewer registers that contain basic functions in applications where the full functionality of the Standard ZPA Mode Assemblies is not required. The Reduced Size Assemblies provide basic accumulation and release control along with module diagnostic data while removing the interfaces for reading/writing tracking data.
ZPA Mode Inputs to PLC
Module Address | Register Name | Assembled Modbus Address | Assembled EIP Address | Assembled Profinet Address |
---|---|---|---|---|
4:0116 | Local Status Upstream Zone | 4:2900 | I.Data [0] | Byte 0 (Hi) Byte 1 (Lo) |
4:0196 | Local Status Downstream Zone | 4:2901 | I.Data [1] | Byte 2 (Hi) Byte 3 (Lo) |
4:0106 | Arrival Count Local Upstream Zone | 4:2902 | I.Data [2] | Byte 4 (Hi) Byte 5 (Lo) |
4:0107 | Departure Count Local Upstream Zone | 4:2903 | I.Data [3] | Byte 6 (Hi) Byte 7 (Lo) |
4:0186 | Arrival Count Local Downstream Zone | 4:2904 | I.Data [4] | Byte 8 (Hi) Byte 9 (Lo) |
4:0187 | Departure Count Local Downstream Zone | 4:2905 | I.Data [5] | Byte 10 (Hi) Byte 11 (Lo) |
4:0088 | Module Status Word 1 | 4:2906 | I.Data [6] | Byte 12 (Hi) Byte 13 (Lo) |
4:0089 | Module Status Word 2 | 4:2907 | I.Data [7] | Byte 14 (Hi) Byte 15 (Lo) |
4:0105 | Current Release Count for Upstream Zone | 4:2908 | I.Data [8] | Byte 16 (Hi) Byte 17 (Lo) |
4:0185 | Current Release Count for Downstream Zone | 4:2909 | I.Data [9] | Byte 18 (Hi) Byte 19 (Lo) |
4:0035 | Sensor & Control Port Inputs | 4:2910 | I.Data [10] | Byte 20 (Hi) Byte 21 (Lo) |
Reserved | 4:2911 | I.Data [11] | Byte 22 (Hi) Byte 23 (Lo) |
ZPA Mode Outputs from PLC
Module Address | Register Name | Assembled Modbus Address | Assembled EIP Address | Assembled Profinet Address |
---|---|---|---|---|
4:0104 | Accumulation Control for Local Upstream Zone | 4:3000 | O.Data [0] | Byte 0 (Hi) Byte 1 (Lo) |
4:0184 | Accumulation Control for Local Downstream Zone | 4:3001 | O.Data [1] | Byte 2 (Hi) Byte 3 (Lo) |
4:0040 | Set Left MDR Speed | 4:3002 | O.Data [2] | Byte 4 (Hi) Byte 5 (Lo) |
4:0064 | Set Right MDR Speed | 4:3003 | O.Data [3] | Byte 6 (Hi) Byte 7 (Lo) |
4:0105 | Release and Accumulate on Next Arrival for Local Upstream Zone | 4:3004 | O.Data [4] | Byte 8 (Hi) Byte 9 (Lo) |
4:0185 | Release and Accumulate on Next Arrival for Local Downstream Zone | 4:3005 | O.Data [5] | Byte 10 (Hi) Byte 11 (Lo) |
4:0134 | Set Status for Upstream Induct | 4:3006 | O.Data [6] | Byte 12 (Hi) Byte 13 (Lo) |
4:0232 | Set Status for Downstream Discharge | 4:3007 | O.Data [7] | Byte 14 (Hi) Byte 15 (Lo) |
4:0022 | Clear Motor Error | 4:3008 | O.Data [8] | Byte 16 (Hi) Byte 17 (Lo) |
4:0063 | Set Control Port Outputs | 4:3009 | O.Data [9] | Byte 18 (Hi) Byte 19 (Lo) |
Reserved | 4:3010 | O.Data [10] | Byte 20 (Hi) Byte 21 (Lo) |
|
4:0109 | Clear Sensor Jam Command for Local Upstream Zone | 4:3011 | O.Data [11] | Byte 22 (Hi) Byte 23 (Lo) |
4:0189 | Clear Sensor Jam Command for Local Downstream Zone | 4:3012 | O.Data [12] | Byte 24 (Hi) Byte 25 (Lo) |
4:0365 | Direction & Accumulation Mode Control for Local Upstream Zone | 4:3013 | O.Data [13] | Byte 26 (Hi) Byte 27 (Lo) |
4:0375 | Direction & Accumulation Mode Control for Local Downstream Zone | 4:3014 | O.Data [14] | Byte 28 (Hi) Byte 29 (Lo) |