Table 1 – Specifications

Specification Conditions 24 Vdc 48 Vdc 130 Vdc 260 Vdc
Industry Standards (designed to) standard applications IEEE 2405-2022
NEMA PE-5
Agency
Listings (labeled)
standard features & options CSA C22.2
UL 1012
UL 1564
Output Voltage Regulation Vac +10%, -12%
0 to 100% load
frequency 60 ± 3 Hz
(0 to 122 °F / -18 to 50 °C)
± 0.25%
(see product literature for specific data)
Transient Response 10-90% load change, with battery connected (per NEMA PE-5)
Output Ripple Voltage Filtered (with battery, at battery terminals) 30 mV 30 mV 100 mV 200 mV
Filtered (without battery) 1% rms 2% rms
Eliminator (without battery) 30 mV 30 mV 100 mV 200 mV
Special 30mV Eliminator Filter (with 130V battery) n/a n/a 30 mV n/a
Current Limit Adjustable 50-110% of rated output current
Soft Start 0 to 100% Load 4 seconds
Surge Withstand Capability test per ANSI C37.90.1-1989 no erroneous outputs
Reverse Current from Battery ac input power failure (tbd)
Audible Noise average for four (4) sides, 5 ft / 1.5m from enclosure less than 65 dBA

Table 2 – Specifications, Continued

Specification Conditions 24 Vdc 48 Vdc 130 Vdc 260 Vdc
Environment cooling natural convection for (6-25Adc) & (15-100Adc)
ambient temperature operating 0 to 122 °F / -18 to 50 °C
elevation 3000 ft / 1000m without de-rating
relative humidity 0 to 95% non-condensing
pollution degree PD2
installation category Category III
ingress NEMA Type 1 (standard)
Alarm Relay Contact Rating 120 Vac 0.5 A resistive
AC Input Voltage (value on nameplate) +10%, -12% (of nominal)
Efficiency 16-25 Adc rating, full load (%) n/a n/a n/a 92.3%
30-50 Adc rating, full load (%) 82.2% 88.7% 92.7% n/a
75 Adc rating, full load (%) 74.7% 82.5% 92.7% n/a
100 Adc rating, full load (%) 74.7% 82.5% n/a n/a
Last modified: 12 September 2023