Tag Name Data Type Module Register Bit Description
I_ArrivalUPZn BOOL 4:0116 AOI Logic Arrival at Local Upstream Zone – Only active if zone becomes occupied and it has been set to accumulate
I_ArrivalDNZn BOOL 4:0196 AOI Logic Arrival at Local Downstream Zone – Only active if zone becomes occupied and it has been set to accumulate
I_ControlPortPin3_Left BOOL 4:0035 1 Left Control Port Pin 3 Energized
I_ControlPortPin3_Right BOOL 4:0035 3 Right Control Port Pin 3 Energized
I_ControlPortPin4_Left BOOL 4:0035 5 Left Control Port Pin 4 Energized
I_ControlPortPin4_Right BOOL 4:0035 7 Right Control Port Pin 4 Energized
I_ConveyStopByLeftControlPort BOOL 4:0020 8 ConveyStop Activated at Local Left Control Port
I_ConveyStopByLostConnection BOOL 4:0020 6 ConveyStop Activated because of Lost Connection
I_ConveyStopByPLCCmd BOOL 4:0020 7 ConveyStop Activated because of PLC Command
I_ConveyStopByPLCDisconnect BOOL 4:0020 10 ConveyStop Activated because of Lost PLC Connection
I_ConveyStopByRemoteModule BOOL 4:0020 5 ConveyStop Activated by another module in Stop Group
I_ConveyStopByRightControlPort BOOL 4:0020 9 ConveyStop Activated at Local Right Control Port
I_GetForwardTracking DINT 4:0201 (MSW) 4:0202 (LSW) - Current Forward Tracking Value at Induct to Local Upstream Zone
I_Heartbeat BOOL 4:0035 15 Module Heartbeat
I_JamAtUPZn BOOL 4:0088 5 Sensor Jam at Local Upstream Zone
I_JamAtDNZn BOOL 4:0089 5 Sensor Jam at Local Downstream Zone
I_ModuleEnabled BOOL - - Local ERSC Module Output are Enabled
I_ModuleFault BOOL 4:0088 4:0089 AOI Logic Module Fault Active (Logical OR of bits 2,4,and 7 from 5-6 and bits 2 and 7 from 5-7

I_ModuleStatus DINT 4:0088 (MSW) 4:0089 (LSW) Modules Status Words 1 and 2
I_MtrError_Left BOOL 4:0088 3 Left Motor Error is Active
I_MtrError_Right BOOL 4:0089 3 Right Motor Error is Active
I_SensorPortPin3_Left BOOL 4:0035 0 Left Sensor Port Pin 3 Energized
I_SensorPortPin3_Right BOOL 4:0035 2 Right Sensor Port Pin 3 Energized
I_SensorPortPin4_Left BOOL 4:0035 4 Left Sensor Port Pin 4 Energized
I_SensorPortPin4_Right BOOL 4:0035 6 Right Sensor Port Pin 4 Energized
I_TrackingDNZn DINT 4:0199 (MSW) 4:0200 (LSW) - Current Tracking Value for Arrival at Local Downstream Zone
I_TrackingUPZn DINT 4:0119 (MSW) 4:0120 (LSW) - Current Tracking Value for Arrival at Local Upstream Zone
I_ZoneStatusDnZn SINT 4:0196 Lo Byte Zone Status Local Downstream Zone Forward Direction
I_ZoneStatusUpZn SINT 4:0116 Lo Byte Zone Status Local Uptream Zone Forward Direction