Register Name / Module Address Assembled Address for PLC Description
ConveyStop Command Word
4:0020
M: 4:1619
E: O.Data [19]
P: Byte 38 (Hi)
   Byte 39 (Lo)
Integer Value:
   0 = No Command
   1 = Command local module’s Stop Group to
       go to Stopped State
   2 = Command Local Module’s Stop Group to
       Clear Stopped State
Clear Sensor Jam for Local Upstream Zone
4:0109
M: 4:1620
E: O.Data [20]
P: Byte 40 (Hi)
   Byte 41 (Lo)
Use when PLC detects a local Upstream jam in Module Status Word #1 Bit 5:
   PLC creates transition from 0 to 1 to send command to local upstream zone to clear the jam condition
Clear Sensor Jam for Local Downstream Zone
4:0189
M: 4:1621
E: O.Data [21]
P: Byte 42 (Hi)
   Byte 43 (Lo)
Use when PLC detects a local Downstream jam in Module Status Word #2 Bit 5:
   PLC creates transition from 0 to 1 to send command to local downstream zone to clear the jam condition

Sensor Jam Clear Commands

These registers are applicable only to a Sensor Jam condition. By default, in ZPA mode, the ERSC will attempt 3 times to automatically clear a sensor jam and if the sensor is still blocked, the ERSC will stop the zone. To reset this condition the Carton must be manually removed after the 3rd attempt and the sensor cleared before the zone will return to normal operation.
These registers allow the PLC to remotely attempt another auto-clear cycle in an attempt to clear the jam condition. Please note that this function requires the PLC to make a transition from 0 to 1 in the register to initiate another auto-clear cycle. Holding the value to 1 will not cause the retry to continue indefinitely. Each attempt requires a new transition from 0 to 1