NOTICE TIME ZONE | Brisbane UTC +10 |
---|---|
STATUS (Open/Closed) | Closed |
INCIDENT CAUSED BY A 3RD PARTY? | No |
IF YES, NAME OF 3RD PARTY | N/A |
INCIDENT START DATE | 20230829 |
INCIDENT START TIME (HH:MM) | 15:23 |
ESTIMATED TIME TO RESOLUTION | |
INCIDENT END DATE | 20230829 |
INCIDENT END TIME (HH:MM) | 16:12 |
INCIDENT TOTAL DURATION | 49 minutes |
XCRM TICKET NUMBER | Not Applicable |
BRAND | XNET |
PRIORITY | P1 |
CLIENTS AFFECTED | All Clients |
DESCRIPTION OF INCIDENT | All Services |
EVENT TIMELINE | |
Tuesday 29th August 2023 | |
15:23 | XSTRA Monitoring indicates all communications at NEXDC B2 are down |
15:35 | Technician has been despatched to NEXTDC B2 site – ETA 25 minutes |
15:55 | Hardware determined at fault |
16:10 | Hardware replaced |
RECOVERY & RESOLUTION | Hardware replaced |
ROOT CAUSE | Mikrotik CRS 1036 in boot loop |
CORRECTIVE & PREVENTATIVE MEASURES | N/A – hardware will fail at some point – replacement hardware was ready and pre-configured for efficient and timely swap out |