The following table lists the Binary Input Status registers:
Modbus Binary Input Status Registers | ||
---|---|---|
Address | Name/Description | If Status is ‘ON’ (Logic ‘1’) |
10001 | High Voltage DC (HVDC) Alarm | active |
10002 | Low Voltage DC (LVDC) Alarm | active |
10003 | DC Output Failure Alarm | active |
10004 | No AC Input Alarm (no zero-crossing detected) | active |
10005 | Positive Ground Fault Alarm | active |
10006 | Negative Ground Fault Alarm | active |
10007 | Common Alarm Relay (CAR) Alarm | active |
10008 | High Voltage DC (HVDC) Shutdown Active | active |
10009 | Low Voltage AC (LVAC) Shutdown (<65% nominal Vac) | active |
10010 | Forced Load Sharing Enabled | enabled |
10011 | Temperate Compensation (TempCo) Enabled | enabled |
10012 | Defective Temperate Probe | defective |
10013 | Equalize Mode (0 = float) | equalize |
10014 | (not used) | - |
10015 | (not used) | - |
10016 | Auto-Equalize Timer | enabled |
10017 | HVDC Shutdown Enabled | enabled |
10018 | (not used) | - |
10019 | High Ripple Alarm | active |
10020 | End of Discharge Alarm | active |
10021 | Rectifier Over Temperature Alarm | active |
10022 | DC Breaker Status | open |
10023 | External Voltage Sense Fail Alarm | active |
10024 | Internal Voltage Sense Fail Alarm | active |
10025 | DC Power Supply Alarm | active |
10026 | Open DC Output Alarm | active |
10027 | High Level Detect Alarm | active |
10028 | Low Level Detect Alarm | active |
10029 | Low AC Supply Alarm (<75% nominal Vac) | active |
10030 | Current Limit Status | active |
10031 | High Level Detect Shutdown Status | active |
10032 | Alarm Relay Failure | active |
10033 | Rectifier Temperature Sense Failure | active |
10034 | Display / UI Processor Failure | active |
10035 | Battery Open Alarm | active |
10036 | Loadshare Communication Failure | active |
10037 | Loadshare Independent Mode | active |
10038 | Loadshare Not Ready | active |
10039 | Battery Discharging | discharging |
10040 | Battery Overtemp | => setpoint |
10041 | Vgnd Imbalance Warning | => setpoint |
10042 | Vgnd Imbalance Critical | => setpoint |
10043 | Positive Ground Fault Warning | res to gnd <= setpoint |
10044 | Negative Ground Fault Warning | res to gnd <= setpoint |
10045 | Dynamic Current Limit | active |
10046 | Power Board EEROM Failure | failed |
10047 | Main EEROM Failure | failed |
10048 | Hardware Level Detect Digital Potentiometer Failure | potentiometer failed |
10049 | Ambient Temperature Probe Failure | probe failed |
10050 | Open AC Breaker | tripped |
10051 | AC Meter Option Installed | installed |
10052 | AC Supply (1PH or 3PH) | three phase |
10053 | Low Priority Alarm | active |
10054 | High Priority Alarm | active |
- | future | - |