The following table lists Analog Inputs (Object 30).

It is important to note that 16-bit and 32-bit variations of Analog Inputs, Analog Output Control Blocks, and Analog Output Statuses are transmitted through DNP as signed numbers. Even for analog input points that are not valid as negative values, the maximum positive representation is 32767.

The “Multiplier” column indicates the value by which each data point is multiplied. Since all data points are sent in integer format, floating point numbers are multiplied by a constant (1, 10, or 100) to maintain decimal information. For example, points with two decimal places of resolution are multiplied by 100 (5.67 is sent as 567) while points with one decimal place of resolution are multiplied by 10 (8.2 is sent as 82). To convert a data point to the correct value, simply divide the point by the “Multiplier” value.

The “Default Deadband” column is used to represent the absolute amount by which the point must change before an analog change event will be generated. The “Default Event Class” column is used to represent the class (1, 2, 3, or none) in which detected change events will be reported. Only the default values for these columns are shown here because the values may change in operation due to either local (user-interface) or remote (through DNP) configuration control.

Analog Input Status Points
Static (Steady-State) Object Number 30
Change Event Object Number 32
Reporting Deadband Object Number 34
Request Function Codes supported: 1 (read)
2 (write) – deadbands only
22 (assign class)
Static Variation reported when variation 0 requested: 2 (16-bit Analog Input)
Change Event Variation reported when variation 0 requested: 2 (Analog Change Event without Time)
Reported Deadband Variation Reported when variation 0 requested 1 (16-bit Reporting Deadband)
Change Event Scan Rate: 5 seconds
Point Index Name/Description Multiplier (format) Default Deadband Default Event Class
0 Display / UI Processor Firmware Rev 1 (XXX.xxx.0) 1 2
1 DNP Firmware Rev 1 (XXX.xxx.0) 1 2
2 Main ATevo Processor Firmware Rev 1 (XXX.xxx.0) 1 2
3 ATevo Model Nominal Output Voltage Rating (Vdc) 1 (XXX) 1 2
4 ATevo Model Nominal Output Current Rating (Adc) 1 (XXX) 1 2
5 Charger DC Output Voltage (Vdc) 10 (XXX.X) 1 2
6 Charger DC Output Current (Adc) 10 (XXX.X) 1 2
7 Equalize Time Remaining (minutes) 1 (XXXX) 1 2
8 (not used) 1 (XXXXX) 1 2
9 Battery Temperature (°C) 10 (XXX.X) 1 2
10 Rectifier Temperature (°C) 10 (XXX.X) 1 2
11 Vgnd Imbalance Lean
(1 – pos(+) > 5%, 2 – neg(-) > 5%, 0 – less than 5%)
1 (X) 1 2
12 Positive Terminal to Ground 1 (XXXXX) 1 2
13 Negative Terminal to Ground 1 (XXXXX) 1 2
14 Vgnd Imbalance (Vdc) 10 (XXX.X) 1 2
15 Resistance to Ground (kOhms)
(1 – pos(+) to gnd, 2 – neg(-) to gnd, 0 – invalid)
1 (X) 1 2
16 Loadshare Enabled
(1 – primary, 2 – secondary, 0 – not enabled)
1 (X) 1 2
17 Battery Open Test Timestamp Low (seconds since January 1, 2000) 1 (XXXXX) 1 2
18 Battery Open Test Timestamp High (seconds since January 1, 2000) 1 (XXXXX) 1 2
19 Ambient Temperature (°C) 10 (XXX.X) 1 2
20 Heartbeat 1 (XXXXX) 1 2
21 AC Input Voltage – Phase A (Vac) 10 (XXXX.X) 1 2
22 AC Input Voltage – Phase B (Vac) 10 (XXXX.X) 1 2
23 AC Input Voltage – Phase C (Vac) 10 (XXXX.X) 1 2
24 AC Input Current – Phase A (Aac) 10 (XXXX.X) 1 2
25 AC Input Current – Phase B (Aac) 10 (XXXX.X) 1 2
26 AC Input Current – Phase C (Aac) 10 (XXXX.X) 1 2
27 AC Line Frequency (Hz) 100 (XXX.XX) 1 2
28 Battery Current (Adc) 10 (XXXX.X) 1 2
- future - - -
  • Upper 8 bits of register value are the Major Version
  • Lower 8 bits of register value are the Minor Version
  • Example: Version 10.6.0 would be 0×0A06 (hex) = 2566 (decimal)
Last modified: 25 October 2023