Table 1 – Specifications
Specification | Conditions | 24 Vdc | 48 Vdc | 130Vdc | 260 Vdc |
---|---|---|---|---|---|
Output Voltage Regulation | Vac +10%, -12% 0 to 100% load frequency 60 ± 3 Hz (0 to 122 °F / -18 to 50 °C) |
± 0.25% (see product literature for specific data) |
|||
Transient Response | 10-90% load change, with battery connected | (per NEMA PE-5) | |||
Output Ripple Voltage | Filtered (with battery, at battery terminals) | 30 mV | 30 mV | 100 mV | 200 mV |
Filtered (without battery) | 1% rms | 2% rms | |||
Battery Eliminator (without battery) | 30 mV | 30 mV | 100 mV | 200 mV | |
Super Eliminator Filter (with battery) | n/a | n/a | 30 mV | n/a | |
Current Limit | Adjustable | 50-110% of rated output current | |||
Soft Start | 0 to 100% Load | 4 seconds | |||
Surge Withstand Capability | test per ANSI C37.90.1-1989 | no erroneous outputs | |||
Reverse Current from Battery | ac input power failure | (tbd) | |||
Audible Noise | average for four (4) sides, 5 ft / 1.5m from enclosure | less than 65 dBA |
Table 2 – Specifications, Continued
Specification | Conditions | 24 Vdc | 48 Vdc | 130Vdc | 260 Vdc |
---|---|---|---|---|---|
Environment | cooling | natural convection for (16-300Adc) forced air internal fan for (400-1000Adc) |
|||
ambient temperature | operating 0 to 122 °F / -18 to 50 °C | ||||
elevation | 3000 ft / 1000m without de-rating | ||||
relative humidity | 0 to 95% non-condensing | ||||
pollution degree | PD2 | ||||
installation category | Category III | ||||
ingress | NEMA Type 1 (standard) | ||||
Alarm Relay Contact Rating | 120 Vac | 0.5 A resistive | |||
AC Input Voltage | (value on nameplate) | +10%, -12% (of nominal) |