The relationship between the external voltage at input 0-10V and the motor speed is linear in the range of the minimum and maximum speeds of the MDR (580 – 5800) RPM for ECO and (580 – 4200) RPM for BOOST Mode. The table below shows the 22 sample values at equal intervals.
No. | 0-10V Input |
ECO Mode Motor RPM |
BOOST Mode Motor RPM |
Open Loop PWM % |
---|---|---|---|---|
1 | 0.00 V | 580 | 580 | 10.00% |
2 | 0.50 V | 580 | 580 | 10.00% |
3 | 1.00 V | 580 | 580 | 10.00% |
4 | 1.50 V | 870 | 630 | 15.00% |
5 | 2.00 V | 1160 | 840 | 20.00% |
6 | 2.50 V | 1450 | 1050 | 25.00% |
7 | 3.00 V | 1740 | 1260 | 30.00% |
8 | 3.50 V | 2030 | 1470 | 35.00% |
9 | 4.00 V | 2320 | 1680 | 40.00% |
10 | 4.50 V | 2610 | 1890 | 45.00% |
11 | 5.00 V | 2900 | 2100 | 50.00% |
12 | 5.50 V | 3190 | 2310 | 55.00% |
13 | 6.00 V | 3480 | 2520 | 60.00% |
14 | 6.50 V | 3770 | 2730 | 65.00% |
15 | 7.00 V | 4060 | 2940 | 70.00% |
16 | 7.50 V | 4350 | 3150 | 75.00% |
17 | 8.00 V | 4640 | 3360 | 80.00% |
18 | 8.50 V | 4930 | 3570 | 85.00% |
19 | 9.00 V | 5220 | 3780 | 90.00% |
20 | 9.50 V | 5510 | 3990 | 95.00% |
21 | 10.00 V | 5800 | 4200 | 100.00% |
22 | 11.00 V | 5800 | 4200 | 100.00% |