!This document assumes the user is aware of MDR power requirements for the application and that the user and/or installer have properly sized 24VDC power supplies and wiring based upon all applicable codes and standards. This document also assumes installation will follow proper equipment grounding practices. “DC common or -”on all power supplies should always be connected to ground. Improper power supply sizing and/or improper grounding practices will produce unexpected results.
Power Connector Plug |
Part Number |
Degson 8EDGK-35-03P-11 |
Wire Size |
28 – 14 AWG (0.2 – 1.5 mm 2) |
Strip Length |
5 – 6 mm |
Regardless of the specific ConveyLinx-ECO Module, each is equipped with the ability to separate the Motor power from the Logic power.
Connecting only Motor Power
*Connecting only to Motor Power will provide power to both the motor circuits and the logic circuits.
Connecting Motor Power and Logic Power Separately
*Providing a separate power connection to the Logic Power, you can keep the logic and communications powered and active and disconnect the Motor Power to assure all motors are disconnected such as in an E-Stop situation