There may be instances when you want to return a ConveyLinx-ECO Module to its “factory default” state. The procedure to do this requires you connect to the module with EasyRoll:

  1. Go to the Advanced Dialog and select the Network Services tab
  2. Click the Discover button
  3. Select the module you wish to return to Factory Default settings from the list
  4. Click the Restore Factory Settings button

Factory Default Settings

Item Value or Setting
IP Address Settings IP: 192.168.21.20
Subnet Mask: 255.255.128.0
Default Gateway: 192.168.21.1
Left & Right Motor Settings Normal Braking
80% Rated Speed
Closed Loop
CW Direction
30 Pulses Acceleration
30 Pulses Deceleration
Module Mode PLC I/O
Look Ahead & Timing Settings JAM Timer = 0.00
Auto Clear Timer = 5.00
Run After Timer = 0.00
Sensor Debounce = 0.10
All Induct Timers = 0.00
Sensors Sensors are “ON is Blocked”
Connections All are Cleared

Feedback