There are 3 receive PDOs utilized by the MotionLinx-Ai module. This is the data that originates from the master controller that is received by the MotionLinx-Ai module.

Receive PDO0 – Motor Setup (Object 0×1600)

Subindex Index Data Type Data Description
SubIndex 1
Motor Control Left
Index 0×2000
SubIndex 0
SINT Bit 0:
  ON = Run Command
   OFF = Stop Command
Bit 1:
   OFF = Run in Configured Direction
   ON = Run opposite of Configured Direction
SubIndex 2
Motor Control Right
Index 0×2000
SubIndex 0
SINT
SubIndex 3
Motor Speed Left
Index 0×2001
SubIndex 0
INT Integer value to set the motor speed
   • For MDR the value is in mm/sec
   • For PGD the value is in motor RPM
SubIndex 4
Motor Speed Right
Index 0×2001
SubIndex 0
INT
SubIndex 5
Motor Brake Mode Left
Index 0×200F
SubIndex 0
SINT Integer value to set the motor braking method
   • See Motor Braking Methods Chart
SubIndex 6
Motor Brake Mode Right
Index 0×2010
SubIndex 0
SINT

Motor Braking Methods Chart

Value Method Data Description
0 Normal Once the controls have decelerated the rotor to a stop, the motor coils are internally connected. The permanent magnet forces in the rotor and the mechanical inertia of the gearbox holds the rotor in place. This is the industry standard holding brake method and is often termed short circuit or shunt. Normal is the default factory setting for all Pulseroller control modules.
1 Free Once the controls have decelerated the rotor to a stop, the motor coils are internally disconnected and only the mechanical gearbox inertia holds the rotor in place.
2 Servo When the controls have decelerated the rotor to a stop, the processor notes the Hall Effect sensor status. If the Hall Effect sensor status changes indicating a change in rotor position, the controls will inject current into the motor coils in the proper sequence to move the rotor back to its original stop position



Receive PDO1 – Motor Ramps (Object 0×1601)

Subindex Index Data Type Data Description
SubIndex 1
Motor Acceleration Left
Index 0×2003
SubIndex 0
INT Integer value to set the acceleration/deceleration ramps for Left/Right motor
   • For MDR the value is in mm
   • For PGD the value is in motor pulses
SubIndex 2
Motor Deceleration Left
Index 0×2004
SubIndex 0
INT
SubIndex 3
Motor Acceleration Right
Index 0×2005
SubIndex 0
INT
SubIndex 4
Motor Deceleration Right
Index 0×2006
SubIndex 0
INT

Receive PDO2 – Servo/Periphery (Object 0×1602)

Subindex Index Data Type Data Description
SubIndex 1
Servo Control
Index 0×2007
SubIndex 0
INT Bit 0: Reset Command Left Motor
   0 to 1 = Set Current Position as “0”
Bit 1: Servo Run Command Left Motor
   1 = Run motor from current position value to value in Set Motor Servo Left SubIndex
Bit 8: Reset Command Right Motor
   0 to 1 = Set Current Position as “0”
Bit 9: Servo Run Command Right Motor
   1 = Run motor from current position value to value in Set Motor Servo Right SubIndex
SubIndex 2
Set Motor Servo Left
Index 0×2008
SubIndex 0
INT Signed integer value to move to on the next Servo Run Command Left/Right Motor
   • Values are in mm for MDR
   • Values are in motor pulses for PGD
   • Valid values are from -32767 to +32767
SubIndex 3
Set Motor Servo Right
Index 0×2009
SubIndex 0
INT
SubIndex 4
Set Sensor Port Pin 2 Outputs
Index 0×2011
SubIndex 0
Byte If either or both Sensor ports have been configured as Outputs this numerical value controls their digital state:
   0 = Both OFF
   1 = Energize Left Sensor Port Pin 2 Only
   2 = Energize Right Sensor Port Pin 2 Only
   3 = Energize Both
SubIndex 5
Clear Motor Error
Index 0×2012
SubIndex 0
Byte Numerical value to clear a motor error on either or both Motor Ports:
   0 to 1 = Clear Motor Error
If there is a motor error present, the module must see a transition from 0 to 1 to clear the error. Maintaining a constant value of 1 will not automatically clear a motor error if it occurs.