RaptorLinx-Ai-ST Controller / Controller Hardware /
LED Status Indicators
RaptorLinx-Ai-ST status is indicated by several LED’s. All LED’s with the exception of the Ethernet Link and Activity LEDs are multi-colored and context sensitive. The following sections indicate the various meanings of all LED indicators.
Indicator | Item | LED State | Description |
M8 Sensors | |
Solid GREEN | Sensor Input is energized |
Solid AMBER | Module is booting up | ||
Solid RED | Aux I/O Pin 2 is energized (when configured as an Input) | ||
Flashing RED | Network Stop condition active | ||
Flashing AMBER | Power supply is less than 10V | ||
Slow Blinking RED | Profinet enabled discover function initiated from PLC | ||
Module Status | |
Solid RED | Module is booting up or during Auto-Replacement procedure, module is attempting to retrieve data from neighbor module(s) |
Blinking RED | Module is starting task processes | ||
Blinking GREEN | Module is Ready | ||
Flashing GREEN & Blinking RED | Auto-replace procedure has been properly triggered | ||
Flashing RED & Blinking GREEN | Failsafe Mode | ||
Flashing RED | Auto Configure Mode is active | ||
Blinking AMBER | Performing firmware upgrade check | ||
Solid AMBER | Firmware upgrade in progress | ||
Network Status | |
Solid RED | Starting Inter-module communications |
Blinking RED | Establishing inter-module connections | ||
Blinking GREEN | Inter-module communications established | ||
Digital Inputs | Solid GREEN | Sensor Input is energized | |
Solid AMBER | Module is booting up | ||
Flashing RED | Network Stop condition active | ||
Flashing AMBER | Power supply is less than 10V | ||
Slow Blinking RED | Profinet enabled discover function initiated from PLC | ||
Digital Output | |
Solid GREEN | Output is Energized |
Slow Flash RED | Output Fault or Short Circuit | ||
Motor | |
OFF | Motor is not running and no faults detected |
Solid ON GREEN | Motor is running | ||
Solid ON RED | If Motor is running – indicates current limit If Motor is stopped – indicates motor is not connected properly or is overheated Power supply is under 18V or above 30V |
||
Slow Blink RED | Motor is overloaded and the module is limiting current to reduce temperature | ||
Slow Flash RED | Motor short circuit detected between at least two of the phase windings or Motor Power supply is less than 10V |
Indicator States
Indication | Rate | Visible Action |
Slow Blink | 1 Hz | 500 msec. ON / 500 msec OFF |
Fast Blink | 2.5 Hz | 200 msec. ON / 200 msec OFF |
Slow Flash | 2 Hz | 250 msec. ON / 250 msec OFF |
Fast Flash | 10 Hz | 50 msec. ON / 50 msec OFF |
Single Flash | 200 msec. ON / 1000 msec OFF | |
Double Flash | 200 msec. OFF / 200 msec ON / 1000 msec OFF |